Are their any relaying concerns or set backs in regards to the simultaneous faulting of two circuits sharing the same tower? Or with other types of relaying?
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
submonkey said:Hi Mbrooke,
Modelling mutual coupling is not that
hard, and it can be done by hand - it
is just rather tedious to check all the
different cases.
The mutual impedance has units of ohms,
or "volts per amp". In the case of zm0,
the mutual impedance tells you how many
zero sequence volts induced in feeder 1
per amp on feeder 2.
You could model this by inserting an appropriate transformer in your
equivalent circuit model.
From what I've read and seen, power system
engineers from the fifties, sixties and
seventies seemed to have a much better
grasp of fundamental theory than the current
generation.
Having said that, one could probably get
away with a lot by making (conservative)
educated guesses. Mutual coupling always
makes the zone 1 reach setting shorter and
the zone 2 reach setting longer.
Alan
bacon4 life said:Before widespread event recording, there wasn't much to go on for determining correct relay versus incorrect relay operation. Once we started analyzing high speed recordings, there were a number of events where the correct breakers opened, but some of the internal relay elements did not actually operate as intended.
submonkey said:Hi Mbrooke,
It is usually zero sequence mutual coupling
which has an impact. I think it would be
easiest to insert a transformer (or coupled
inductors) within the zero sequence equivalent
circuits. Sequence networks are always balanced, and so are considered "per phase".
The concept of wye wye does not really apply.
Submonkey said:Regarding the quantitative impact of mutual
coupling - I won't give any numbers here for
fear that someone may actually use them. If you do a few setting studies for mutually
coupled lines, you will get a feel for the
typical values.
Also worth mentioning are cases where fault
current flows "forwards" on one side of a tower line, and "backwards" on the partner
line. In these cases the coupling effect is
much stronger than when one line is earthed.
It's important to understand the physical
arrangement of the lines, and where the fault
current flows. I usually look at our GIS maps
and sketch up the arrangement before commencing a study.
Thanks,
Alan
David Beach said:A cycle or so for the relay and 2-3 cycles for breaker time plus, maybe, a bit of slop. I like to list the longer end of the time range but I do see the occasional fault that is cleared in 3 cycles (relay + breakers) with a 3 cycle breaker. But I also see a 3 cycle breaker sometimes take an extra cycle or two if it's been closed for a very long time and the go just 3 cycles on the second trip.
Piterpol said:MBrooke, you can find among SEL Application Guides that identified with number AG95-29, Dated on 20140611, and authored by Armando Guzman, Jeff Roberts, and Karl Zimmerman, Volume I, entitled "Applying the SEL-321 Relay to Permissive Overreaching Transfer Trip (POTT) Schemes. Read pages from 8 to 12 and you will find very clearly explained Current Reversals under "POTT Scheme Complications and Solutions.