I have a 130 MW STG in a CCGT plant application that experienced high cycle fatigue failure of several of the L-0 buckets in less than 8700 hours of operation. OEM is stating that 4 separate events of low vacuum opertion caused this failure (a total of 21 minutes in duration), The last low vacuum event occured 2 weeks before the failure (over an 11 minute period of time). Profilometry inspection of the failure surface indicated that the crack growth during this 11 minute period of time was insignificant. We did a whole battery of metalurgical tests and examinations that still support HCF.
One item that we found was that there was more than 20 % variation in the area check (measured at 3 points from the radius) of the L-0 diaphragm and as much as a 12 % variation in the area check of the L-1 diaphragm. We are thinking that the poor area check control by the manufacturer could have created enough pulsations to excite the L-0 blades, considering that the blade design only has a 5.8% margin at the 1X natural frequency. It might be important to note that this is a 60 Hz application with a STG specification requirement for the STG to operate at 60 Hz +/-5% without limitation.
Has any other user out there been able to correlate Area Check variation in stationary diaphragms with resonance excitation of downstream blades? What levels of acceptable area variations are user seeing in STG diaphragms? What margin of safety off of the 1X and 2X natural frequency is typically being seen on new LP blade designs?
Thanks
One item that we found was that there was more than 20 % variation in the area check (measured at 3 points from the radius) of the L-0 diaphragm and as much as a 12 % variation in the area check of the L-1 diaphragm. We are thinking that the poor area check control by the manufacturer could have created enough pulsations to excite the L-0 blades, considering that the blade design only has a 5.8% margin at the 1X natural frequency. It might be important to note that this is a 60 Hz application with a STG specification requirement for the STG to operate at 60 Hz +/-5% without limitation.
Has any other user out there been able to correlate Area Check variation in stationary diaphragms with resonance excitation of downstream blades? What levels of acceptable area variations are user seeing in STG diaphragms? What margin of safety off of the 1X and 2X natural frequency is typically being seen on new LP blade designs?
Thanks