AISC 13th Sect J10 has a number of requirements that need to be checked when you have point loads on flanges, including flange local bending, web local yielding, etc, etc.
Most of these can be strengthened with the use of transverse stiffener pairs (perpendicular to the web). Per section J10.8, "...compressive forces... design in accordance with the requirements of Sctions E6.2 and J4.4. The member properties shall be determined using an effective length of 0.75 h and a cross section composed of two stiffeners and a strip of web having a width of 25tw..."
I'm designing a plate girder supporting some pretty serious concentrated forces. In lieu of using one really thick stiffener - I'd like to use several smaller stiffeners, say 5 pairs, spread out over the width of the applied force. I had been running calculations ignoring the "strip of web" but feel like I`m missing out on some strength here, but using a width of 25tw would overlap, or double count, some web sections.
I'd like to use a strip of web equal to 1/2 the stiffener spacing in each direction. Does anybody see any problems with this procedure?
Alternatively - I could use member properties for the entire 5-stiffener pairs with the web extending 12.5tw past the end of each stiffener pairs, but I believe this will provide much more strength than the above and doesn't intuitively feel right to me.
Most of these can be strengthened with the use of transverse stiffener pairs (perpendicular to the web). Per section J10.8, "...compressive forces... design in accordance with the requirements of Sctions E6.2 and J4.4. The member properties shall be determined using an effective length of 0.75 h and a cross section composed of two stiffeners and a strip of web having a width of 25tw..."
I'm designing a plate girder supporting some pretty serious concentrated forces. In lieu of using one really thick stiffener - I'd like to use several smaller stiffeners, say 5 pairs, spread out over the width of the applied force. I had been running calculations ignoring the "strip of web" but feel like I`m missing out on some strength here, but using a width of 25tw would overlap, or double count, some web sections.
I'd like to use a strip of web equal to 1/2 the stiffener spacing in each direction. Does anybody see any problems with this procedure?
Alternatively - I could use member properties for the entire 5-stiffener pairs with the web extending 12.5tw past the end of each stiffener pairs, but I believe this will provide much more strength than the above and doesn't intuitively feel right to me.