aseeng
Structural
- Jun 17, 2013
- 22
I am looking for opinions and current practice for design of wood floor framing with stone veneer on top. I am aware of the Marble institute criteria for L/720 deflection. I understand this to be a total load requirement. Similarly I have criteria out there for tile and stone floors that talk about the 300 lb. point load deflection requirement. Further the criteria looks less stringent for concrete slabs as they behave differently than wood. Some thoughts I have;
1. It seems to me that as you lay in the stone and grout it the dead load deflection is already there prior to setting up. Wouldn't the critical deflection criteria be for live load only?
2. The different criteria for concrete slabs sounds reasonable when considering live load and how it will distribute that load. But for a given span on a one way slab L/360 results in a certain deflection and curvature that is no different than for wood framing in regards to total load. What is the difference?
3. We look at at this situation on exterior decks with high snow loading. It is one thing to size the joists for this criteria but then the beam sizing really gets out of hand when considering full snow loads. We assume the criteria should extend to the beams as well as just the joists? Correct?
4. What about steel beams? Same criteria? I know we have not strictly followed the L/720 for these members where larger live load areas are concerned.
We know there are a lot of designs out there that don't strictly meet this criteria but we are not aware of any performance issues either. Any other experiences out there?
Thanks for your replies.
1. It seems to me that as you lay in the stone and grout it the dead load deflection is already there prior to setting up. Wouldn't the critical deflection criteria be for live load only?
2. The different criteria for concrete slabs sounds reasonable when considering live load and how it will distribute that load. But for a given span on a one way slab L/360 results in a certain deflection and curvature that is no different than for wood framing in regards to total load. What is the difference?
3. We look at at this situation on exterior decks with high snow loading. It is one thing to size the joists for this criteria but then the beam sizing really gets out of hand when considering full snow loads. We assume the criteria should extend to the beams as well as just the joists? Correct?
4. What about steel beams? Same criteria? I know we have not strictly followed the L/720 for these members where larger live load areas are concerned.
We know there are a lot of designs out there that don't strictly meet this criteria but we are not aware of any performance issues either. Any other experiences out there?
Thanks for your replies.