Electrical
Nov 24, 2010
13
HI

we have to store some electrical/electronic control cabinets for aorund 7 yrs,


can anyone help with recommendations for storage, conditions , silicon seal, that kind of detail

thanks
 
Replies continue below

Recommended for you

Pure metal? As dry as possible. Rubber seals? Minimum humidity to keep them supple without rusting any metal.

Dan - Owner
Footwell%20Animation%20Tiny.gif
 
Macg

sorry, more detail,

yep, mild steel box, with door seal. Is painted RAL,

good idea on low humidity

 
Silica gel bags inside cabinet. Shrink-wrap the cabinets. Store them in a low humidity environment.


----------------------------------
image.php

If we learn from our mistakes I'm getting a great education!
 
I hope there aren't a lot of electrolytic capacitors - they may need reforming or replacing after sitting that long.

xnuke
"Live and act within the limit of your knowledge and keep expanding it to the limit of your life." Ayn Rand, Atlas Shrugged.
Please see FAQ731-376 for tips on how to make the best use of Eng-Tips.
 
There are some mil standards applicable to storage. I don't recall the numbers off-hand. The requirements can be extreme. I've got some old surplus synchros that were literally canned. I opened one to peek, and it was like new after about 50 years.

Beware of ESD if wrapping systems with non-ESD plastic. Exposed connector pins combined with massive static charge could cause damage.

 
hi guys,

thanks for replies, some good tips there,

the main electronics is a 3 phase inverter drive,

this is the official storage data from the manufacturer

Storage
• Store within an ambient temperature range of -40° to +85°C.
• Store within a relative humidity range of 0% to 95%,
non-condensing.
• Do not expose to a corrosive atmosphere.

such a range in temp, humidity, seems crazy,

ScottyUK

like :Silica gel bags inside cabinet. Shrink-wrap the cabinets. Store them in a low humidity environment.

 
If the VFD is going to be stored for more than a year, you will need to either power it up on occasion or plan on reforming the capacitors before putting it in service.

"If I had eight hours to chop down a tree, I'd spend six sharpening my axe." -- Abraham Lincoln
For the best use of Eng-Tips, please click here -> faq731-376
 
The range in temperature and humidity is not for a single site, but for any site, worldwide, which is typical of military specifications as well. The cold temp would be consistent with NK or Siberia, while the hot temps would be consistent with the Middle East.