Strange auto reclose sequence

Status
Not open for further replies.
Replies continue below

Recommended for you

Three is more typical I'd agree.

I'd chock it up to those NOT being recloser events but some other thing like swinging wires or tree-sway. The ground fault actually didn't look very big. Maybe 20 or 30kW so line protection might not have gotten involved at all.

Keith Cress
kcress -
 
Maybe a very short reclaim timer on the recloser? Since the fault took ~8 seconds to clear each time, a reclaim timer of 7 or fewer seconds would force the relay to see this as many separate reclose events instead of part of a single series. We use a longer reclaim timer, but we have had trouble with circuits reclosing several times during storms when an intermittent fault takes more than 30 seconds to reoccur.
 
Short reclaim is my guess. Is it possible the primary and secondary relays are "fighting" one another?
 
I have seen five re-closures.
Three short time closures to clear birds, rodents and tree branches.
Two additional longer time closures to allow a fuse to open on a shorted distribution transformer.
I agree. This doesn't fit that pattern either.

Bill
--------------------
"Why not the best?"
Jimmy Carter
 
Could be a circuit to circuit fault. One recloser cycles while the other resets, then swap.
 
Could be, never thought of that one lol :)
 
Could be a circuit to circuit fault.
Could that involve the fence?

Bill
--------------------
"Why not the best?"
Jimmy Carter
 
A large number of reclosing attempts presented in this video is unusual and dangerous for life safety and potential equipment damage.

There is a trend in the power utility industry to reduce the numbers of reclosing to 2 or 3 reclosing attempts. Notice that survey below, no utility reported 4 attempts.

....................
Reclosing_Attempts_m942qu.jpg
..................
 