triden
Electrical
- Jan 21, 2020
- 3
I have a system with some submersible pumps that are fed by some Siemens Sirius soft starts. Pumps are 125HP @ 600vac. When we run the pump, the softstart gets up to speed like normal (5s ramp) and the bypass contactor pulls. Within about 10 minutes they start overloading and tripping (some trip within 30 seconds). I checked the current on each leg on the load and supply side of the starter and get the following readings:
L1: 119A
L2: 151A
L3: 128A
Quite the imbalance. Just for the fun of it, we swung the transfer switch over and ran the station on genset power. All phase currents were perfectly balanced with no issues. Pumps didn't overload or trip and were very happy.
Swung back to the utility and major current imbalance again. Measured phase to ground on each leg and got within 5vac which is very close...so doesn't seem like a voltage issue. The problem is the same for all pumps in the station.
Anyhow, power company came up and said everything was fine. Clearly it's not. What do you think could be the cause of this?
L1: 119A
L2: 151A
L3: 128A
Quite the imbalance. Just for the fun of it, we swung the transfer switch over and ran the station on genset power. All phase currents were perfectly balanced with no issues. Pumps didn't overload or trip and were very happy.
Swung back to the utility and major current imbalance again. Measured phase to ground on each leg and got within 5vac which is very close...so doesn't seem like a voltage issue. The problem is the same for all pumps in the station.
Anyhow, power company came up and said everything was fine. Clearly it's not. What do you think could be the cause of this?