TSun
Electrical
- Mar 8, 2013
- 9
I recently came across a double ended 480 service entance switchboard with both mains closed and the tie open. surge protection is installed on both service entances. Each surge protector is equipped with a surge counter. The surge counter from one substation recorded around 10 surges, the other counter indicated over 300. I reset the counters and checked back a month or so later. I found one counter showing only a handful of surges and one showing hundreds. Both services are supplied by dry type transformers fed from an entirely underground system with multiple levels of surge peotection and some high end meterng that would have picked up any surges on the distribution system. Essentially I can rule out any causes external to the building. The building only has 'typical' commercial building loads, motors, lights, etc... No low voltage pf corection, transformers tapped at nominal. Any thoughts on what could be the cause? This isn't the first tim. I have seen this either. Several other buildings in the area have similar installations and show the same problem.
Thanks for your help.