I have been investigating a building where the slab-on-grade was placed about a month ago and only a portion of it has some cracks. The building is a long, fairly narrow footprint (sort of like an apartment building - where the slab was placed in three separate pours. The center 1/3 is cracking.
Here's some relevent data:
1. 4" thick
2. Placed on 4" sand
3. Compaction tests of subbgrade all ok.
4. Center 1/3 area was placed with retarder in 1/2 of it (contractor said 30 minute retarder) and then the last half had 60 minute retarder.
5. f'c = 4500 psi (I agree its high for a SOG)
6. Concrete used a steel fiber reinforcing throughout (no WWF in the slab).
7. Contractor stated that in their area they have had a cement shortage and the source of the cement had shut down operations for a time, and then fired up again - he thinks that the cement they used in the center 1/3 was produced after the shutdown and he got some reports that the cement was "hot". Not the concrete being hot in the truck - but the cement was hot or too fresh.
8. The placement finished with a thunderstorm which thoroughly wetted the slab for the rest of the day - Curing compound placed the next day after the slab dried a bit.
9. No idea on aggregate size.
I've never heard of "hot" or too-fresh cement before causing cracks - is this a valid reason for excess shrinkage or are there any other thoughts on this? Cracks are fairly spaced out and fairly large (1/8" to 3/16"). Many project out of re-entrant corners of the building and other floor openings so I'm pretty confident its shrinkage.
Here's some relevent data:
1. 4" thick
2. Placed on 4" sand
3. Compaction tests of subbgrade all ok.
4. Center 1/3 area was placed with retarder in 1/2 of it (contractor said 30 minute retarder) and then the last half had 60 minute retarder.
5. f'c = 4500 psi (I agree its high for a SOG)
6. Concrete used a steel fiber reinforcing throughout (no WWF in the slab).
7. Contractor stated that in their area they have had a cement shortage and the source of the cement had shut down operations for a time, and then fired up again - he thinks that the cement they used in the center 1/3 was produced after the shutdown and he got some reports that the cement was "hot". Not the concrete being hot in the truck - but the cement was hot or too fresh.
8. The placement finished with a thunderstorm which thoroughly wetted the slab for the rest of the day - Curing compound placed the next day after the slab dried a bit.
9. No idea on aggregate size.
I've never heard of "hot" or too-fresh cement before causing cracks - is this a valid reason for excess shrinkage or are there any other thoughts on this? Cracks are fairly spaced out and fairly large (1/8" to 3/16"). Many project out of re-entrant corners of the building and other floor openings so I'm pretty confident its shrinkage.