Hello everyone,
I work at a power plant and we have an issue regarding the oil of a main transformer.
The transformer is 18/161kV, 400MVA.
About two months ago, oil was purified in a transformer and it was returned to work. Recently we have seen an increase in the concentration of hydrogen in the oil up to about 200 ppm and the concentration continues to rise. There is also evidence of an increase in CO and CO2. It should be noted that there is no increase in concentrations of other flammable gases.
According to the conclusions of a chemical laboratory, this is a "STRAY GASSING" phenomenon in which oil itself distributes hydrogen when it is heated.
My questions:
1. How long will the increase in hydrogen concentrations continue until it stabilizes?
2. Will a decrease in the oil temperature cause a decrease in the hydrogen concentration? If so, where is the distributed hydrogen going? The transformer is sealed.
3. I have heard about "inhibitor" oil supplement that may reduce STRAY GASSING phenomenon. Does anyone have any information on this? Is it recommended? What is the recommended compound?
Thank you.
I work at a power plant and we have an issue regarding the oil of a main transformer.
The transformer is 18/161kV, 400MVA.
About two months ago, oil was purified in a transformer and it was returned to work. Recently we have seen an increase in the concentration of hydrogen in the oil up to about 200 ppm and the concentration continues to rise. There is also evidence of an increase in CO and CO2. It should be noted that there is no increase in concentrations of other flammable gases.
According to the conclusions of a chemical laboratory, this is a "STRAY GASSING" phenomenon in which oil itself distributes hydrogen when it is heated.
My questions:
1. How long will the increase in hydrogen concentrations continue until it stabilizes?
2. Will a decrease in the oil temperature cause a decrease in the hydrogen concentration? If so, where is the distributed hydrogen going? The transformer is sealed.
3. I have heard about "inhibitor" oil supplement that may reduce STRAY GASSING phenomenon. Does anyone have any information on this? Is it recommended? What is the recommended compound?
Thank you.