I have encountered a situation in which a measurable ground
exists in a low voltage power system. The system is a 277/480 Vac three phase power system derived through a 2000 kva transformer fed from a 13.2kv service. The transformer neutral is solidly grounded. The main breaker has ground fault relaying. The existing measured currents are below the rating for the ground fault sensors. The current has been measured on a number of the equipment ground conductors (with clamp on CT's and Data logging equipment) that are in the conduits with the feeders. Ground currents have also been measured on the ground grid conductors on the bonding conductor to the transformer neutral. The currents vary in magnitude over time but we cannot correlate it to any equipment stopping or starting in the process. This substation is part of an industrial facility that operates 24-7 so troubleshooting is difficult. The majority of the load served is 3 phase consisting of motor loads (some with VFD's), process resistive loads and 480/120 Vac distribution transformers. There is some 277V lighting however this load was isolated and meggared during an earlier phase of the troubleshooting effort. No grounds were detected in the lighting systems. The power distribution feeders are for the most part in underground conduits routed through a manhole system. This condition has been going on for some time since first detected (months).
My experience says that I would suspect that there is obviously a high resistance ground in the system. However, my experience over the last twenty years in the engineering and maintenance business is that ground faults on solidly grounded systems generally develop quickly into damaging phase to phase or three phase faults if not cleared by the ground fault protection. Usually the damage and resultant equipment outage is easy to find.
We plan to ground check all feeders at the next available downtime.
However because I have never experienced a solidly grounded system behave like this I would also like to get some other opinions on what else could possibly explain the situation and what other things we should investigate.
exists in a low voltage power system. The system is a 277/480 Vac three phase power system derived through a 2000 kva transformer fed from a 13.2kv service. The transformer neutral is solidly grounded. The main breaker has ground fault relaying. The existing measured currents are below the rating for the ground fault sensors. The current has been measured on a number of the equipment ground conductors (with clamp on CT's and Data logging equipment) that are in the conduits with the feeders. Ground currents have also been measured on the ground grid conductors on the bonding conductor to the transformer neutral. The currents vary in magnitude over time but we cannot correlate it to any equipment stopping or starting in the process. This substation is part of an industrial facility that operates 24-7 so troubleshooting is difficult. The majority of the load served is 3 phase consisting of motor loads (some with VFD's), process resistive loads and 480/120 Vac distribution transformers. There is some 277V lighting however this load was isolated and meggared during an earlier phase of the troubleshooting effort. No grounds were detected in the lighting systems. The power distribution feeders are for the most part in underground conduits routed through a manhole system. This condition has been going on for some time since first detected (months).
My experience says that I would suspect that there is obviously a high resistance ground in the system. However, my experience over the last twenty years in the engineering and maintenance business is that ground faults on solidly grounded systems generally develop quickly into damaging phase to phase or three phase faults if not cleared by the ground fault protection. Usually the damage and resultant equipment outage is easy to find.
We plan to ground check all feeders at the next available downtime.
However because I have never experienced a solidly grounded system behave like this I would also like to get some other opinions on what else could possibly explain the situation and what other things we should investigate.