mar2805
Structural
- Dec 21, 2008
- 372
Hi guys!
I need some advice.
Please see picture atttached.
As you can see its an existing RC slab spaning in one direction.
Slab is supported by masonry bearing walls
The thickness is UNBELIVABLE for the given span. Only 5 inches!
The slab is said to me reinforced in bottom and top layer allthou I have my doubts in how the hell did they manage to put 2 layers of reinforcement in such a thin slab.
Ive done some calculations by hand and using FEM software and the reason for that large crack in the top layer of the support is clear.
There isnt enough reinforcement in the slab to satisfy the bending moment in the slab.
The problem now is that both, the bottom layer and the top layer were reinforced using the same area (said by the constructor).
Since thers a crack formed in top of the slab, the negative bending moment will tend to go to zero value and in return the positive bending moment in the bottom of the slab will increase (since this will become a simply supported slab system).
I calculated that the reinforcement in the bottom of the slab isnt capable of resisting "increased" positive bending moment, BUT the slabs hasnt started cracking yet on the bottom side.
These are good news.
I need to strenghten the slab.
My idea was to cast RC beam under the slab.
There would need to be 3 beams for each field spaning in the short direction.
This would be done by making formwork for beams under the slab and by pouring concrete thru holes that would be made in the RC slab.
Theres 3 beams would lower the bending moments in the slab to an value that is small enough for the reinforcement to resist it.
We have done some FEM modeling and analysis modeling the new RC beams that are not "monolitical tied" with the slab.
The numbers seem fine but there a lot of questions that are bothering me...
Has anyone done such a thing already?
Thank you
I need some advice.
Please see picture atttached.
As you can see its an existing RC slab spaning in one direction.
Slab is supported by masonry bearing walls
The thickness is UNBELIVABLE for the given span. Only 5 inches!
The slab is said to me reinforced in bottom and top layer allthou I have my doubts in how the hell did they manage to put 2 layers of reinforcement in such a thin slab.
Ive done some calculations by hand and using FEM software and the reason for that large crack in the top layer of the support is clear.
There isnt enough reinforcement in the slab to satisfy the bending moment in the slab.
The problem now is that both, the bottom layer and the top layer were reinforced using the same area (said by the constructor).
Since thers a crack formed in top of the slab, the negative bending moment will tend to go to zero value and in return the positive bending moment in the bottom of the slab will increase (since this will become a simply supported slab system).
I calculated that the reinforcement in the bottom of the slab isnt capable of resisting "increased" positive bending moment, BUT the slabs hasnt started cracking yet on the bottom side.
These are good news.
I need to strenghten the slab.
My idea was to cast RC beam under the slab.
There would need to be 3 beams for each field spaning in the short direction.
This would be done by making formwork for beams under the slab and by pouring concrete thru holes that would be made in the RC slab.
Theres 3 beams would lower the bending moments in the slab to an value that is small enough for the reinforcement to resist it.
We have done some FEM modeling and analysis modeling the new RC beams that are not "monolitical tied" with the slab.
The numbers seem fine but there a lot of questions that are bothering me...
Has anyone done such a thing already?
Thank you