Strengthening of existing steel beam under load 1

Status
Not open for further replies.

isidor_

Civil/Environmental
Aug 30, 2022
14
I am controlling the capacity of some existing beams in a structure for new loads. The beams are welded I sections, ~13m long, simply supported and it looks as if they will need reinforcing.

Some restrictions, limitations and other info
New columns cannot be added to reduce the span length.
They are under load and the load cannot easily be reduced as there is activity.
Temporary offloading by jacking up the beams is possible but not easy as the beam/slab is the third story.
They are only accessible from below, so only the bottom flange, the web and the underside of the top flange.
(Some of) The beams are already deflecting about 50mm, which limits the strengthening procedures, for example a "perfectly straight" section cant be inserted into or attached to the curved beam I assume.
The strengthening cannot add too much depth below the bottom flange.
The beams are quite tall and slender, 600-800mm tall with flanges about 350mm with a thin web.
The beams are primary beams, secondary beams are connected to them and brace them laterally at a few points reducing their buckling lengths.
Located in the EU if it makes a difference

I have searched and found some relevant threads but have a few questions.
Strengthening methods:
1. Welding of cover plates, I was thinking about adding a plate below the bottom flange, the plate being wider than the flange to get good (easier) welding from above. The plate could also be fitted in accordance with the curvature.
Since it is under load, any welding will cause the section to soften due to the heat which I assume adds deflection. How much of an issue is this?​
Since it is under load the bottom flange is already under tension stresses, while the new material should have (close to) no stresses, will this discrepancy cause issues?​
If the cover plate is welded without (partially) unloading the beam, then the added material will only effect additional loads?​
2. FRP reinforcement.
While I (personally) cannot do this, I could recommend it to the customer if it is feasible, is this a viable solution to recommend? It adds no heat, is lighter/easier to handle than additional (heavy) steel profiles, seems less of a project than welding aswell​
3. Post tensioning of the steel beam
I have (briefly) read some texts about this and it seems good. If done properly it seems to me that i could even remove some of the deformations on the beam. For instance adding a kingpost type of solution​
How is the connection properly done to the beam? Welding something to the thin web seems hazardous​
Regarding the detailing, the image below shows three examples.
The first one should be easiest to do since it would only attach to the bottom flange. But since the bottom flange is bent downwards wouldn't the prestressing cause it to bend further down? (I know it is below the NA so it gives a negative moment that should cause the beam to bend upwards, but part of my brain worries I am missing something...​
The second is the option I prefer, aside from the web connection at the ends ofc. The stiffeners where the tendon changes direction takes a compressive force upwards from the node causing the beam to elevate.​
Welding will be required here but will be more localized at the "nodes" so that is an positive at least​
Screenshot_2_srtq1v.png


Thanks in advance and hope my English is sufficient to convey the questions.
Any input into the matter is appreciated.
 
Replies continue below

Recommended for you

Isidor_:
Using Koot’s truss configuration, if you put a turnbuckle or a pulling jack at the mid-length of his horiz. bot. chord, you would draw the bot. tips of the two end triangles together, thus jacking up (lifting) the deflection out of the existing beam. The trick would be designing the end triangle clamping device/hardware out near the end of the existing beam and checking the beam for buckling/stability during this operation. This assumes a single bot. flg. doubler pl. would solve your stress problem for the new loads. You clamp the doubler pl. to the bot. of the existing flg., then you install the left and right truss triangles under the beam, and pull them together enough to eliminate the existing bm. deflection, then do the welding to the flg. There are a few calcs. and some construction methods thinking btwn. each of these steps.
 
I might've missed it somewhere in this thread, but is the reinforcing required for any of the existing load? Or is only for new load? And is the new load going to be mostly dead load or live load?

I think a bit more info about the existing dead and live loads with what the new loads will be is a help to figure out the best solution.
 
I made a previous post but I have some additional comments.

I think that one important thing is the utilization for the existing beam with the existing loads and what is the failure mode?

When you add material the new material will be stress free. That assumes that you just add material, nothing else is done. When you add load the existing material will probably have an increase in stresses, the new material will get stresses. If you have some margin the increase may be acceptable. If you don't, what is the failure mode? If the failure is stability related, you probably need to add something that stabilizes. If the problem is yielding, that may be acceptable.

You mentioned that the load can not be easily reduced. If the existing situation includes a high utilization, reducing the load may be easier for reducing the stresses in the existing structure then other methods.

And how do you plan to design this structure? Is the issue with ULS or SLS, or both? I find it hard to believe that you should have a constant ULS-load situation, or am I missing something?
 