Do wee need to use stress cones (Termination kit) for MV Tray cables 4.16kV and 23kV.

Please share your knowledge and recommendation.
thanks,
Kani
 
Replies continue below

Recommended for you

Yes, Cable termination (stress cones ) for 4.16 & 23 kV system should be installed to manage the excess of electric fields created at the cable end.
Below is an example of the EMF Stress release with & without cable termination.
Cable_Termination_MV_Relief_E_Field_Stresses_issw2s.jpg
 