I have recently been involved with a discussion regarding the use of stress cones on 5kV motor leads for a particular motor.
The first part of the discussion regarded weather or not stress cones were needed on 5kV cable. I was always under the impression that these kits were indeed needed on 5kV cables and was looking for a standard or reference to back me up since he was arguing otherwise. Are these stress cones required on all 5kV shielded cables? Is it legal or a good practice to use non-shielded MV cable for a 5kV cable run?
The second part of the discussion regarded how motor leads were terminated onto a 5kV motor. Because this motor does not have a surge caps or arrestors there is not bus connection at the motor to terminate the motor leads or motor feeders on. Therefore a Motor Lead Pigtail Splice kit was used with the motor feeders and motor leads bolted together. This kit does not have a ground around the shield at the end of the motor feeder cable to tie to ground at the motor. I was under the impression that you indeed needed to tie the shield to ground at "BOTH" ends of the cable to ensure uniform charge distribution at both ends, and dont present a path for charge flux to go out the end of the cable. The contractor is arguing that as long as shield is grounded at the source end then this is o.k.
Also as one last point, this motor happens to be a 6-lead motor that is connected to our source in a wye configuration. When connecting the T4,T5,T6 leads together for the wye configuration there was no splie kits or any other kits used and it was just bolted and taped. I know that if everything is blanced there will be no voltage at this wye point, but for an unbalanced condition there may be a voltage with respect to ground at this point. Does this junction need some kind of kit as well?
I would appreciate any insight into this application.
The first part of the discussion regarded weather or not stress cones were needed on 5kV cable. I was always under the impression that these kits were indeed needed on 5kV cables and was looking for a standard or reference to back me up since he was arguing otherwise. Are these stress cones required on all 5kV shielded cables? Is it legal or a good practice to use non-shielded MV cable for a 5kV cable run?
The second part of the discussion regarded how motor leads were terminated onto a 5kV motor. Because this motor does not have a surge caps or arrestors there is not bus connection at the motor to terminate the motor leads or motor feeders on. Therefore a Motor Lead Pigtail Splice kit was used with the motor feeders and motor leads bolted together. This kit does not have a ground around the shield at the end of the motor feeder cable to tie to ground at the motor. I was under the impression that you indeed needed to tie the shield to ground at "BOTH" ends of the cable to ensure uniform charge distribution at both ends, and dont present a path for charge flux to go out the end of the cable. The contractor is arguing that as long as shield is grounded at the source end then this is o.k.
Also as one last point, this motor happens to be a 6-lead motor that is connected to our source in a wye configuration. When connecting the T4,T5,T6 leads together for the wye configuration there was no splie kits or any other kits used and it was just bolted and taped. I know that if everything is blanced there will be no voltage at this wye point, but for an unbalanced condition there may be a voltage with respect to ground at this point. Does this junction need some kind of kit as well?
I would appreciate any insight into this application.