Elecman,
Thanks for your comments, you have been most helpful and have provided answers to all of my questions. By the sounds of your posting, you have been involved in similar installations. It is really good and helpful to hear how installations similar to the one I am involved with have been done, successfully.
In particular, thank you for making me aware of the vibration issue. This alone will preclude the use of PILS type cable. At this stage, the power cable to each of the platforms is planned to be at 11kV and to be included in the "umbilical" to each platform and so would be either XLPE or EPR insulated. EPR sounds to be a better way to go.
I also concur with your comments about manufacturers, it is a good general comment applicable to all areas.
BJC,
Thank you for your comments. Supply at DC as per your suggestion would be viable for some applications I think, but not really for my one for various reasons:
(1) No wish to put in a 600V or 1000V DC system at the onshore point of supply. This would have to be a dual redundant system to satisfy maintenance and reliability requirements.
(2) There are reliability issues with inverters, you would probably need to have two of these on each platform as well.
(3) The whole of the platform will be a hazardous area. It would be necessary to attempt to house the inverters in explosion proof enclosurers on the platform and this may be a problem.
(4) For these sorts of applications, simplicity really pays and it is difficult to beat 11kV supply plus cable to transformer plus DB. Hazardous area transformers, 11kV switchgear and 400V DB's, although hellishly expensive, are all available as standard production items from a range of vendors.
Regards