wag2483
Structural
- Oct 28, 2009
- 11
In lieu of stop logs a contractor has proposed a plate to retain water. The plate would drop into vertical notches that were originally cast into an 8' x 8' concrete conduit. The design approach is to treat the plate in horizontal strips acting simply supported. To be determined, but anticipated that the plate may require stiffeners, angles welded horizontally at a given space on center. Preliminary calcs confirmed that when the angles are positioned on the tension side of plate, opposite water pressure, both the PNA and ENA fall within the plate thickness, meaning the angles will only see tension. Is it then acceptable to design in accordance with AISC steel const. spec F11? Thanks for any suggestions.