submersible pumps on VFD 1

Status
Not open for further replies.

HamidEle

Electrical
Feb 20, 2007
309
Our client specification calls for an isolation transformer on LV VFD output side. This VFD is for the submersible pump application. Don't understand what the reason behind it. Any input would be appreciated.
 
Replies continue below

Recommended for you

One very real reason is that they may have an RCD installed. The PWM HF capacitive currents is recified in the VFD front end and the RCD thinks it is leakage to ground and trips.

Use either transformer or VFD with sine output, aka sinus drive.

Gunnar Englund
--------------------------------------
100 % recycled posting: Electrons, ideas, finger-tips have been used over and over again...
 
A transformer can provide isolation and also makes a very good sinewave filter.
 
In a lot of deep well submersibles, the motor voltage is stepped up to help reduce voltage drop down the well. If you are going to do that, might as well be an isolation transformer as opposed to an autotransformer.

"If I had eight hours to chop down a tree, I'd spend six sharpening my axe." -- Abraham Lincoln
For the best use of Eng-Tips, please click here -> faq731-376
 
It might be used to isolate the HF noise generated by the VFD from other transducers that are measuring the level in the bore. Often, the level measuring devices are connected from the bore into ancillary controls and kept away from the VFD. If they are connected to the VFD, they can often 'close the loop' for HF noise in the whole circuit and create additional problems of accuracy.
I have seen this practice a few times.

I also agree with jraef. Boosting the volts the the VFD if the bore depth is long is a means to ensure you have the right volts reaching the motor. Most submersible pumps require you to fit a sinewave filter on the output of the VFD (the motors used often have low insulation quality and need a sinewave/low dvdt) and this output filter will drop the voltage by a few %. This can be critical if the cable is long.
 
Yes Patrick. That is also something that I have seen several times. Several municipal waterworks and sewage works in Sweden are using sine inverters for that reason.

Gunnar Englund
--------------------------------------
100 % recycled posting: Electrons, ideas, finger-tips have been used over and over again...
 
Thanks for the inputs. I will check with our Mechnical engineer if it is a deep well. Most likely not. If it is not a deep well, I would just add a sinewave filter instead of isolation transformer.
 
Except that will do noting to prevent the GFI protection from tripping.

In my opinion it doesn't really matter what we think, speculate the need for, or what you think is reasonable. Your client specified an isolation transformer, so, you should provide one.

Failure to provide one is a good way to inherit all sorts of large legal bills.

Keith Cress
kcress -
 
Yeah, I've never understood all these "my client wants..." threads where somebody wants to argue with the person paying the bills. If it creates problems for you don't take the job, otherwise just provide what is required. Why fight it?
 
If it's a blatant waste or wrong it's our duty to try to help the client "get it right" by educating them, but if the client is dead-set or terminally stupid then I do exactly what they ask for.

Keith Cress
kcress -
 
I don't see an isolation transformer as a blatant waste, wrong, nor terminally stupid. Most of the other 'my client wants..." threads don't fall into those categories either. I think what it is is that the bidder didn't bother to read the specifications and now wants to recover all the money they left on the table. Tuff sh!t.
 
We were doing some work on an existing pilot plant for a Steam Assisted Gravity Drainage system (Sag-Dee). There were several pads and each one had a submersible pump, way down the hole. About half had isolation transformers and the rest had filters. I am sure that this client should know which system he wanted to continue with.
Another possible advantage in this instance was that the transformer driven pumps used 3000 Volt motors rather than 600 Volt motors.
This client should also know which Voltage was most advantageous.

Bill
--------------------
"Why not the best?"
Jimmy Carter
 
davidbeach/itsmoked
I don't think HamidEle is saying the isolation transformer will be left out or is arguing against it, they just want to know the reason for it in this instance.
 
In his 5 Mar 11 1:13 post it sure sounds like he wants to make a substitution.
 
davidbeach
It does, my mistake. HamidEle: I suggest you take the advice given...
 
I did check with one mechanical fellow. It is just slurry submersibale pump,not deep hole pump. I don't think we would need to boost voltage for the motor. The specification from the client is just for that specific application, I believe. We have to make a call whether if it is necesssary to add an isoaltion transformer. HF noise generated by the VFD might be a concern. I will find out more details tomorrow and will discuss here in further detail. Thanks
 
I agree with the others. The client specified it so provide it. I know it pisses me off when someone decides what I specify is "wrong" and they do something different. Even more when their thing doesn't work and I get dragged into the project to solve the problem I didn't cause.
 