jefferslot
Electrical
- Jun 6, 2012
- 8
An industrial cement factory currently takes a supply at 415V 300KVA source (Utility). The existing Earth bonding at the site is substantial and the safety earth is about 0.3ohms.
the owner has now obtained a 1000KVA power transformer ratio 11000/433V with %Z of 4.75%. The utility will shortly be connecting the 11KV supply and has asked if an earthing study has been carried out because the new substation must be classed as HOT (voltage rise of up to 430V).
This is a small industrial plant and I am not sure an expensive detailed earthing analysis is necessary. Anyone had any similar situation?
with substantial bonding and such a low earth value what else would an earthing study reveal?
Jeff
the owner has now obtained a 1000KVA power transformer ratio 11000/433V with %Z of 4.75%. The utility will shortly be connecting the 11KV supply and has asked if an earthing study has been carried out because the new substation must be classed as HOT (voltage rise of up to 430V).
This is a small industrial plant and I am not sure an expensive detailed earthing analysis is necessary. Anyone had any similar situation?
with substantial bonding and such a low earth value what else would an earthing study reveal?
Jeff