If step and touch potential are safe,Why many utility ask for low grid resistance 1 Ω or less for transmission substation?
Please let us know if any comments on:
1) Concern with transfer potential on telephone line in substation. (Today there is fiber optic and better surge protector for isolation).
2) Some engineers are concerned with large GPR=Iground x Rsubimposed imposed on low insulation for auxiliary AC & DC cable and control wires inside the substation.
3) Some engineers were mentioned concern with the zero sequence resistance for relay protection and control. (Not sure if this is an issue with digital relays).
4) Some countries such as Canada limite the GPR for <5 kV. In the USA the IEEE Std 80 have indicative value of 1 Ohm or less indirectly control GPR.