Arentsch
Electrical
- Mar 16, 2009
- 23
We have two 1600A adjacent feeder circuit breakers(CBA3 and CBA4)on a rooftop substation. Both CBA3 and CBA4 feed busducts BD3 and BD4 respectively. Last night CBA4 opened on an Instantaneous fault of 7kA. All loads off of CBA4 were de-energized as expected. However, we also found that a machine fed from a 500A busplug on BD3 had lost it's control power but still had its line power. CBA4 was reset and re-closed. All loads were brought back up one at a time with no issues. Approx. 5 minutes later CBA4 tripped again. The CBA4 trip unit was replaced and CBA4 was re-closed. Again all loads were successfully brought back on one at a time and approx. 5 minutes later CBA4 tripped again. This time it was decided to open and lockout the machine fed from the 500A busplug on BD3 (see the orange box on attached one-line). CBA4 was reset and re-closed and has not tripped again. We would like to get the offending machine back up and running. Any troubleshooting advice or plausible explanations are greatly appreciated. Attached is the one line.