Below is an email I sent to engineering after changing out a bad MW Transducer in one of our stations. I got this data off our server (TOIS) that night via VPN. The XFMR is 30 MVA (161kv/13.8kv) and Regulator is 3333 KVA 10% Raise and Lower. Were all kind of scratching our heads thinking... is this right? This is critical because in August the load was showing 28 MVA in SCADA. We're trying to justify installing a 2nd XFMR.
Question: When the regulator is on 16 lower it lowers the voltage but does it raise the amps on the load side of the regulator and lower the amps on the source side?
"I took these values out of TOIS. It looks like the readings are correct now.
01-OCT-2003 19:15:00 (13.8 Bus kv) 7.8 (Feeder Amps) 157.99 + 118.92 + 149.2 + 167.76 + 159.95 + 147.25 + 168.25 + 164.83 + 184.37 = (Total Amps) 1418
(T1 kv) 8.59 (MVA) -12.09 (MVA1) 10.16 (MW) -11.16 (MVAR) -4.63
The regulator is probably on about 13 lower. Keep in mind that the total current flowing through the metering CT's (in the XFMR) is also the total combined current flowing out of the feeders. However, the regulator has dropped the kv from 8.59 down to 7.8. The MW and MVAR xdcrs are getting their voltage from the 8.59 kv source. To calculate MVA using feeder amps (to compare to SCADA), you have to use 8.59 kv instead of 7.8 kv.
1418 x 8590 = (MVA) 12.18 That's pretty close to the reading in TOIS at 19:15 this evening. Keep in mind that the T1 kv reading may come from the highest of the three T1 kvs.
The point I'm making is, it might look like the MVA reading is too high if you use 7.8 kv value - (1418 x 7800 = 11.06 MVA). On Aug. 17 the load was high enough that the T1 and Bus kvs were close so this wasn't as much of a factor."
Question: When the regulator is on 16 lower it lowers the voltage but does it raise the amps on the load side of the regulator and lower the amps on the source side?
"I took these values out of TOIS. It looks like the readings are correct now.
01-OCT-2003 19:15:00 (13.8 Bus kv) 7.8 (Feeder Amps) 157.99 + 118.92 + 149.2 + 167.76 + 159.95 + 147.25 + 168.25 + 164.83 + 184.37 = (Total Amps) 1418
(T1 kv) 8.59 (MVA) -12.09 (MVA1) 10.16 (MW) -11.16 (MVAR) -4.63
The regulator is probably on about 13 lower. Keep in mind that the total current flowing through the metering CT's (in the XFMR) is also the total combined current flowing out of the feeders. However, the regulator has dropped the kv from 8.59 down to 7.8. The MW and MVAR xdcrs are getting their voltage from the 8.59 kv source. To calculate MVA using feeder amps (to compare to SCADA), you have to use 8.59 kv instead of 7.8 kv.
1418 x 8590 = (MVA) 12.18 That's pretty close to the reading in TOIS at 19:15 this evening. Keep in mind that the T1 kv reading may come from the highest of the three T1 kvs.
The point I'm making is, it might look like the MVA reading is too high if you use 7.8 kv value - (1418 x 7800 = 11.06 MVA). On Aug. 17 the load was high enough that the T1 and Bus kvs were close so this wasn't as much of a factor."