il102
Electrical
- Nov 1, 2011
- 13
There has been some confusion among my peers regarding the following circumstances. Often during the design of a ground grid, an engineer will specify that overhead shield wires from incoming lines must be tied into the ground grid prior to energization for a safe system. I've been told by a few people that tying in these shield wires reduces the ground grid impedance. While this might true in a certain abstract way, I disagree with that notion.
I've even been told by people testing in the field, for example, that the ground grid's impedance was measured at 4 ohms before tying in a shield wire and 2 ohms after tying in a shield wire. I suspect there are more variables at play here. Given the way a ground grid test works (injecting current over a distance in the sub and measuring the voltage drop) I see no physical explanation that would account for this value changing as a result of connecting a random shield wire. The test current won't do anything differently as a result.
It's my understanding that connecting a shield wire ensures that less ground fault current flows into the substation through the earth (rather, a substantial portion comes in through the shield wire). This reduces the safety hazards associated with large amounts of fault current flowing through the earth and instead there is a more efficient, lower resistance path directly through the shield wire - ground grid connection.
But at the end of the day, you can't prove this with a simple measurement in a substation. Is my understanding correct?
Thanks!
I've even been told by people testing in the field, for example, that the ground grid's impedance was measured at 4 ohms before tying in a shield wire and 2 ohms after tying in a shield wire. I suspect there are more variables at play here. Given the way a ground grid test works (injecting current over a distance in the sub and measuring the voltage drop) I see no physical explanation that would account for this value changing as a result of connecting a random shield wire. The test current won't do anything differently as a result.
It's my understanding that connecting a shield wire ensures that less ground fault current flows into the substation through the earth (rather, a substantial portion comes in through the shield wire). This reduces the safety hazards associated with large amounts of fault current flowing through the earth and instead there is a more efficient, lower resistance path directly through the shield wire - ground grid connection.
But at the end of the day, you can't prove this with a simple measurement in a substation. Is my understanding correct?
Thanks!