I used to do a lot of investigations for grain elevators and silos in the miwestern states. A continuous mat spanning 25 meters will be very thick. The most economical foundation, if the soil is strong enough, would be individual ring footings with separate floating floor slabs.
Depending on the height, the stored material, and the method of emptying, the walls may carry a sizeable portion of the live load as well as the dead load.
The silos will tend to tilt towards each other due to the overlap of the pressure bulbs if the soil is uniform, and this may tend to egg-shape the walls, if they touch, or crack the foundation if the silos are separated. If the soil is non-uniform, they may tilt away from each other and try to tear the juncture of the walls.
I assume the silos will be at least as tall as they are wide. Such heavy structures will experience significant settlement unless the soil is unusually strong and incompressible. There will be significant differential settlements that will tend to distort the structures.
The minimum bearing pressure is a function of the weight and the diameter, as a mat can only cantilever about 3 feet beyond the walls.
If you can give us some particulars regarding the type of construction, loads, and soils, we can be more specific. many structures of this type have become distressed or failed entirely; you need guidance from both a geotechnical enginer and a structural engineer with applicable experience.