I've got a 250 thick SOG on good soil. It's going to support some serious rack loads and will be travelled by a fancy cherry picker that runs on guided wires saw cut into the slab. Super flat floor requirements apply.
Our original design was rebar and frequent construction joints.
We met with the GC and the specialist slab placing/finishing contractor. The told us that the way to go was to omit the rebar and use BASF steel pins. More importantly, they said that we should pour the slab in a series of strips the full length of the building (200') with no construction joints perpendicular to the strips. This would involve the use of a low shrinkage concrete mix etc.
The specialist slab contractor advised us that control joints fare very poorly when steel pin reinforcement is used. Curling of the concrete at the saw cut joint. They also pointed out that our flatness requirements are not aesthetic, they are for the benefit of these wire guided lifts. Therefore, a random but small crack in the slab may well be less detrimental than a curled control joint.
We went along with all this more or less. We still haven't decided on the construction joints however. On Friday, we spoke with the company that will be providing the testing machine (one of only four in North America apparently) for assessing the flatness of our floor slab in real time. They seem to be quite expert at this super flat slab business. They recommend that substantial rebar be used as well as frequent, well dowelled construction joints. They too seem to be most worried about curling.
So... does anybody have any experience with super flat slabs that they would be willing to share? Control joints? No control joints? Rebar? No rebar? It's getting to be a bit nebulous for my liking.
Our original design was rebar and frequent construction joints.
We met with the GC and the specialist slab placing/finishing contractor. The told us that the way to go was to omit the rebar and use BASF steel pins. More importantly, they said that we should pour the slab in a series of strips the full length of the building (200') with no construction joints perpendicular to the strips. This would involve the use of a low shrinkage concrete mix etc.
The specialist slab contractor advised us that control joints fare very poorly when steel pin reinforcement is used. Curling of the concrete at the saw cut joint. They also pointed out that our flatness requirements are not aesthetic, they are for the benefit of these wire guided lifts. Therefore, a random but small crack in the slab may well be less detrimental than a curled control joint.
We went along with all this more or less. We still haven't decided on the construction joints however. On Friday, we spoke with the company that will be providing the testing machine (one of only four in North America apparently) for assessing the flatness of our floor slab in real time. They seem to be quite expert at this super flat slab business. They recommend that substantial rebar be used as well as frequent, well dowelled construction joints. They too seem to be most worried about curling.
So... does anybody have any experience with super flat slabs that they would be willing to share? Control joints? No control joints? Rebar? No rebar? It's getting to be a bit nebulous for my liking.