Hello all,
I'm looking for clarification on whether or not I need supplementary reinforcement within a 900x1000mm beam to which a 30mm cast-in shear plate with 30 welded anchor studs (5 rows of 6) is fixed. The studs are 30mm in diameter. There is a shear force of 1400kN acting on the shear plate. Thus far I've completed checks on the anchor, concrete cone pull-out, concrete splitting, blowout (although not necessary as no tension), pry-out and concrete edge, all of which are acceptable.
Given that this is a large force will supplementary reinforcement still be necessary?
I'm looking for clarification on whether or not I need supplementary reinforcement within a 900x1000mm beam to which a 30mm cast-in shear plate with 30 welded anchor studs (5 rows of 6) is fixed. The studs are 30mm in diameter. There is a shear force of 1400kN acting on the shear plate. Thus far I've completed checks on the anchor, concrete cone pull-out, concrete splitting, blowout (although not necessary as no tension), pry-out and concrete edge, all of which are acceptable.
Given that this is a large force will supplementary reinforcement still be necessary?