Hi everyone. I have a question regarding Air changes in occupied space. I am very much clear on Ashrae 62.1 Outdoor air requirements. My concern is about the total supply air changes that is to be maintained in any space. For example: A room has outdoor air requirement of 210 l/s following Ashrae. The total supply air required as per calculations is 270 l/s. The air changes obtained for 270 l/s is around 4.5ACH. Is there any requirement to maintain minimum ACH for supply air? If not then why most of the time we take 1cfm/sq.ft (5 l/s/sq.m) as minimum supply airflow rate in many applications.
 
Replies continue below

Recommended for you

I don't know of any Code-type requirements for SA rates; those are usually driven by cooling load (or in cleanrooms, cleanliness class).
 
There is no requirement for air change requirements, unless code required for healthcare, clean rooms or industrial spaces. The 1.0 cfm/sf is just a rule of thumb for typical cooling CFM for internal spaces for typical spaces such as an office spaces.

knowledge is power
 
Thanks Cdxx and RossABQ. Can I put the same question in other way. If I make load calculations for any space and if I get 0.5cfm/sq.ft as the supply air, Do I need to maintain minimum 1 cfm/sq.ft or the calculated airflow is enough. I read somewhere that minimum 1cfm/sqft (5l/s/sqm) is to be maintained.
 