Graybeard
Chemical
- Jul 10, 2001
- 24
Our plant has had several problems recently related to accurately measuring high temperature (~500C) surfaces using spring loaded flat tip stainless sheathed thermocouples. In several cases the reported surface temperature is up to 100C below what we think the actual temperature is. How? When you have an externally heated vessel or pipe and the material inside the pipe measures higher temperature than measured wall temp, we suspect error. We have moved away from thermocouples welded to wall due to maintenance difficulties. Is anyone else having problems like this? Is there fix/suggestion?