We recently had an outside consultant suggest that we add surge arresters to the H0/X0 (neutral) bushings of our autotransformers. In every case, the neutrals are solidly grounded.
For the case where we have three single-phase transformers connected in a three-phase bank, with the individual H0/X0 brought out to a neutral bus, I can see some logic in having arresters on the H0/X0 bushing, due to the REMOTE possibility of a surge or strike on the conductor between the H0/X0 and the neutral bus. Personally, I feel this is unnecessary, but of course I could be wrong.
However, for a three-phase autotransformer where the H0/X0 is jumpered directly to the ground grid, I see no benefit in a having an arrester on the H0/X0 bushing.
I would love to get some more opinions or best-practices on this.
For the case where we have three single-phase transformers connected in a three-phase bank, with the individual H0/X0 brought out to a neutral bus, I can see some logic in having arresters on the H0/X0 bushing, due to the REMOTE possibility of a surge or strike on the conductor between the H0/X0 and the neutral bus. Personally, I feel this is unnecessary, but of course I could be wrong.
However, for a three-phase autotransformer where the H0/X0 is jumpered directly to the ground grid, I see no benefit in a having an arrester on the H0/X0 bushing.
I would love to get some more opinions or best-practices on this.