Where is the correct position to install a surge arrester.
The equipment to be protected is a 6.6kV motor. Currently there are surge arresters installed in the switchboard (vacuum contactor application). Searching the web it suggests that it is more appropriate to install at the motor but if you have surge suppressor then it is o.k at the switchboard.
I've spent some time reading about surge impedance and travelling pulse waves and then my eyes started to glaze over with all the equations!
Basically we have a number of surge arresters failing and I wondered if there location in the switchboard might be a factor.
Also I am not able to get the BIL insulation rating for the motor, what is a typical value for 6.6kV motor (500kW). I realise typical is not much used but I would like to get a ball park feeling of whether the correct surge arrester is being used.
The other factor is that the network is insulated neutral and the protection did not pick up the failed surge arrester. I wonder if an inappropriate rated voltage has been selected for the arrester and it was failing due to an undetected earthed fault, i.e. increased TOV (temporary over voltage)
The equipment to be protected is a 6.6kV motor. Currently there are surge arresters installed in the switchboard (vacuum contactor application). Searching the web it suggests that it is more appropriate to install at the motor but if you have surge suppressor then it is o.k at the switchboard.
I've spent some time reading about surge impedance and travelling pulse waves and then my eyes started to glaze over with all the equations!
Basically we have a number of surge arresters failing and I wondered if there location in the switchboard might be a factor.
Also I am not able to get the BIL insulation rating for the motor, what is a typical value for 6.6kV motor (500kW). I realise typical is not much used but I would like to get a ball park feeling of whether the correct surge arrester is being used.
The other factor is that the network is insulated neutral and the protection did not pick up the failed surge arrester. I wonder if an inappropriate rated voltage has been selected for the arrester and it was failing due to an undetected earthed fault, i.e. increased TOV (temporary over voltage)