During motor retest following motor removal/replacement, we confirm the direction of rotation by momentarily energizing the motor just long enough to get it rotating.
A fairly knowledgeable engineer recently told me that this can cause excessive surge stresses to the motor. Specifically, the full starting current is still flowing at the time the breaker is re-opened. He said that the interruption of this higher-than-normal current caused excessive voltage surges which could over time damage the insualtion. v=L*di/dt and the i in this case is ~ 6xFLA.
By the way we have mechanical circuit breakers.
I don't know enough about surges and circuit interruption to evaluate this concern. I am skeptical for the following reasons: I was under the impression that this bump test was fairly common practice. Therefore if it were creating severe surges, I would think I would have heard more about it.
What do you guys think?
A fairly knowledgeable engineer recently told me that this can cause excessive surge stresses to the motor. Specifically, the full starting current is still flowing at the time the breaker is re-opened. He said that the interruption of this higher-than-normal current caused excessive voltage surges which could over time damage the insualtion. v=L*di/dt and the i in this case is ~ 6xFLA.
By the way we have mechanical circuit breakers.
I don't know enough about surges and circuit interruption to evaluate this concern. I am skeptical for the following reasons: I was under the impression that this bump test was fairly common practice. Therefore if it were creating severe surges, I would think I would have heard more about it.
What do you guys think?