wirenut60
Electrical
- Jan 26, 2007
- 8
I'm involved in a project where the existing plant distribution is 27kV with a 5kV standby generator. The plant receives power from the utility’s 27kV grounded wye distribution system. The step up transformer between the 27kV bus and the 5kV bus has a delta ungrounded primary, (27kV), and grounded wye secondary (5kV). The original distribution system had MOV surge arrestors on the primary of every 27kV transformer on site. After completion of the generator addition, the plant experienced the failure of most of the MOV surge arrestors that were connected to the plant distribution system when the plant was operated on generator. All MOV surge arrestors were then removed from the 27kV distribution system. I did a little research and found that the MCOV ratings required for 27kV class MOV surge arrestors were not high enough for a ungrounded delta system.
I believe that the step up transformer between the 27kV system and the 5kV generator should have had a wye primary. This would have avoided damage to the MOV arrestors. I have discussed this system with an engineer familiar with, but not directly involved with the generator installation. He maintains there was a reason for this transformer to have the delta primary… but cannot recall the reason. Does anyone know of a reason for installing this transformer with a delta ungrounded primary? I’m starting to think it was installed in error and should have been a wye, or grounded delta, since I do not know of any reason to validate the ungrounded delta primary. Does anyone have some experience on a similar issue?
I believe that the step up transformer between the 27kV system and the 5kV generator should have had a wye primary. This would have avoided damage to the MOV arrestors. I have discussed this system with an engineer familiar with, but not directly involved with the generator installation. He maintains there was a reason for this transformer to have the delta primary… but cannot recall the reason. Does anyone know of a reason for installing this transformer with a delta ungrounded primary? I’m starting to think it was installed in error and should have been a wye, or grounded delta, since I do not know of any reason to validate the ungrounded delta primary. Does anyone have some experience on a similar issue?