I have a situation where there is suspended lighting 15" below ceiling. The lights are 1'-0" wide.
By following the chart in NFPA for floor mounted/suspended obstructions I need to be 24 inches up to 30 inches away from the light in order for spray pattern to clear the fixture.
Is there any way around this? Is there a minimum requirement for a width of an obstruction or anything like that? The problem is the lights are 10'-0" apart so going by that rule, there will be a lot of additional heads just to clear the fixture.
If anyone has any experience/advice it would be greatly appreciated.
By following the chart in NFPA for floor mounted/suspended obstructions I need to be 24 inches up to 30 inches away from the light in order for spray pattern to clear the fixture.
Is there any way around this? Is there a minimum requirement for a width of an obstruction or anything like that? The problem is the lights are 10'-0" apart so going by that rule, there will be a lot of additional heads just to clear the fixture.
If anyone has any experience/advice it would be greatly appreciated.