Swaping to lower size motor on Hitachi SJ300 VFD

Status
Not open for further replies.

krokodiliukas

Electrical
May 24, 2007
1
What settings need to be changed to put 15HP motor instead of current 20HP on Hitachi's SJ300-150LFU. On Altivar VFD's its usually thermal and nominal currents, but on Sj300 manual I found only I0 in H parameters section without explanation.
Thanks
 
Replies continue below

Recommended for you

There has to be somewhere in the drive where you insert motor nameplate data so the overload protection will work.

Using a different size motor simply involves inserting the new nameplate info into the drive. You may want to evaluate the current and torque limits as well.
 