As far as I can figure it, there are two ways to design slender columns in sway frames.
** 1st:
ACI-318 10.11.1
Generaly slender columns could be designed using magnified first order moments.
It shell be permitted (in the absence of more accurate methods) to use moments of inertia reductions: 0.35 for beams and 0.7 for columns.
Correct me if I'm wrong: I can reduce stifnesses of frame members and perform linear, FIRST order analysis.
Obtained forces (factored) I can use for cross-section design (after magnification?).
** 2nd
ACI-318 10.13.3
The moments M_1 and M_2 at the ends of column shell be calculated according to:
M_1 = M_1ns + delta_s * M_1s
M_2 = M_2ns + delta_s * M_2s
where:
M_1s - factor end moment on a compression member at the end at which M_1 acts, due to load that cause no appreciable sidesway, calculated using first order elastic frame analysis (Sway moment)
M_1 - factored end moment
Question:
How to get M_1ns and M_1s?
I understood that non-sway moment results from a vertical load and sway moment from a horizontal load. What if I have load which acts vertical and lateral? Should I split it into two loads and use only vertical component for the M_1ns and horizontal for the M_1s, or should I use complete load to calculate just M_1s?
ACI-318 10.13.4.1
The magnified sway moment (delta_s * M_1s) shell be taken as the column end moment calculated using SECOND order analysis based on the REDUCED member's stifness (10.11.1 - stated above).
What does it mean?
Doesn't that assume that I performed a SECOND order analysis of a whole loading (vertical and horizontal)?
If it does, isn't it in contradiction with 10.11.1 where it is noted that one can use FIRST order analysis with REDUCED stifnesses?
Additionaly, I shell magnify that moment using non-sway procedure (delta_ns):
delta_ns * (M_ns + delta_s * M_s)
SAP2000 uses this (2nd) procedure. It calculates sway and non-sway moments using P-delta analysis (kind of second order analysis), but it does not reduce member's stifness. Is it allowable?
The differences obtained using these two procedures could be drastic. Second procedure reduce stifnesses, calculates second order moments and magnify them.
I'm sure I misunderstood something. Can you help me?
sorry for long question
thanks
** 1st:
ACI-318 10.11.1
** 2nd
ACI-318 10.13.3
where:
Question:
ACI-318 10.13.4.1
What does it mean?