I'm doing a study on a relatively old building and have run across something that I'm not sure how to handle.
The building has a main switchboard which has a design kA rating of 63 kA for 1 second. The main ACB circuit breakers have a Icu / Ics / Icw rating of 75 kA. The board is fed by three emergency generators, each of 2250 kVA at 400 volts, 50 hZ.
Te generators have a subtransient reactance of 12.6%, transient reactance of 17.6% and a zero sequence reactance of 3.16%. The feed from the generators to the switchboard is approximately 30 metres. It is slightly more complex than that as the third generator has lower subtransient and zero sequence impedances.
When I do a calculation I find that the symmetrical RMS short circuit current for a three phase fault is approximately 78 kA, which is above the circuit breaker and board rating. This current drops very rapidly, so that after approximately 1 cycle is is down around 55 kA.
When I do the calculation for the single phase short circuit current (L - E)I get a figure of approximately 88 kA. Again this current falling off rapidly.
I'm not a switchboard person, so my question basically is, what should the fault current rating of the switchboard and the circuit breakers be in this situation?
The building has a main switchboard which has a design kA rating of 63 kA for 1 second. The main ACB circuit breakers have a Icu / Ics / Icw rating of 75 kA. The board is fed by three emergency generators, each of 2250 kVA at 400 volts, 50 hZ.
Te generators have a subtransient reactance of 12.6%, transient reactance of 17.6% and a zero sequence reactance of 3.16%. The feed from the generators to the switchboard is approximately 30 metres. It is slightly more complex than that as the third generator has lower subtransient and zero sequence impedances.
When I do a calculation I find that the symmetrical RMS short circuit current for a three phase fault is approximately 78 kA, which is above the circuit breaker and board rating. This current drops very rapidly, so that after approximately 1 cycle is is down around 55 kA.
When I do the calculation for the single phase short circuit current (L - E)I get a figure of approximately 88 kA. Again this current falling off rapidly.
I'm not a switchboard person, so my question basically is, what should the fault current rating of the switchboard and the circuit breakers be in this situation?