I would appreciate any forum input on the switchboard design issues presented below. I apologize for the length of this thread, but please read on as I believe the issue needs widespread discussion.
I am well aware of the differences between low voltage switchboards and switchgear knowing that Switchboards are tested to a 3 cycle standard and switchgear is tested to a 30 cycle standard. I am also aware that LVPCB's by definition are tested to 30 cycles. Thus the LVPCB and the Switchgear in which the breaker is placed is a fully rated system for 30 cycles when the switchgear is applied within its short circuit ratings.
On the other hand, it seems to me that our industry has not provided concise information to adequately allow users to configure switchboard products since in recent years switchboards are often supplied with main breakers equipped with solid state LSI features. These service entrance main circuit breakers often times include MCCB's as well as LVPCB's and retain their UL 891 Switchboard Listing.
My concern is based on the fact that unlike Switchgear ratings that include both a short circuit withstand rating AND a short time withstand rating, Switchboards do not have a known (or at least published) separate short time withstand rating. Yet most people handed a one line diagram that includes a main service entrance switchboard with a 4000 amp LVPCB main breaker and three 2000 amp LVPCB feeder breakers where all four breakers are equipped with LSI trip units will attempt to set the system up to include short time delays between the main and the feeders.
In the above example and in an effort to provided selective coordination, it has been my experience that a large number of people don't realize they can "turn off" or don't understand what "turning off" the instantaneous feature of the main 4000 amp breaker really does. They of course will still have instantaneous over-ride protection on the newer LVPCB designs for a short circuit on the bus immediately downstream of the 4000 amp main breaker.
But what if the available short circuit current ahead of the selectively coordinated main breaker does not reach the instantaneous override rating of the breaker? For example say the available short circuit current is 50KA and the instantaneous over ride value of the main breaker is 65KA. A short on the load side of the 4000 amp breaker will fall into the short time rating of the main 4000 amp breaker for which there is no published data for the switchboard bus structures. Damaged switchboard bus structures and bus supports are then possible before the 4000 amp breaker clears the 50KA fault.
Likewise, for a through fault condition where the selectively coordinated breaker settings are arranged for a short time delay between the 4000 amp main and the three 2000 amp feeders, the current that flows through the main bus may also result in damaged bus and bus structures due to this short time delay requirement.
In my experience, designers typically don't know about zone interlocking protection or if they do they don't request it often enough under these types of circumstances. Perhaps with focus on arc flash and selective coordination in the 2005 & 2008 NEC, people's understanding of zone interlocking will increase.
Zone Interlocking should help with the short circuit through fault condition described above to prevent short time bus bar and bus support damage in the main switchboard since the feeder breaker is supposed to trip immediately.
On the other hand, if the available short circuit current ahead of the selectively coordinated main 4000 amp breaker is high enough to reach even the Instantaneous Override rating of the main 4000 amp breaker or if the Instantaneous set point of the main 4000 amp breaker is set rather than over ridden, I don't see how a zone interlock system can be fast enough on instantaneous basis to respond to a 65KA through fault condition even with a zone interlock system in place. It seems to me that there would still be a race as to whether or not the 2000 amp feeder or the main 4000 amp breaker opened first because there is no way of knowing if the zone interlock system can communicate quickly enough on an instantaneous basis.
Any comments on this thread would be greatly appreciated.
Thank you.
I am well aware of the differences between low voltage switchboards and switchgear knowing that Switchboards are tested to a 3 cycle standard and switchgear is tested to a 30 cycle standard. I am also aware that LVPCB's by definition are tested to 30 cycles. Thus the LVPCB and the Switchgear in which the breaker is placed is a fully rated system for 30 cycles when the switchgear is applied within its short circuit ratings.
On the other hand, it seems to me that our industry has not provided concise information to adequately allow users to configure switchboard products since in recent years switchboards are often supplied with main breakers equipped with solid state LSI features. These service entrance main circuit breakers often times include MCCB's as well as LVPCB's and retain their UL 891 Switchboard Listing.
My concern is based on the fact that unlike Switchgear ratings that include both a short circuit withstand rating AND a short time withstand rating, Switchboards do not have a known (or at least published) separate short time withstand rating. Yet most people handed a one line diagram that includes a main service entrance switchboard with a 4000 amp LVPCB main breaker and three 2000 amp LVPCB feeder breakers where all four breakers are equipped with LSI trip units will attempt to set the system up to include short time delays between the main and the feeders.
In the above example and in an effort to provided selective coordination, it has been my experience that a large number of people don't realize they can "turn off" or don't understand what "turning off" the instantaneous feature of the main 4000 amp breaker really does. They of course will still have instantaneous over-ride protection on the newer LVPCB designs for a short circuit on the bus immediately downstream of the 4000 amp main breaker.
But what if the available short circuit current ahead of the selectively coordinated main breaker does not reach the instantaneous override rating of the breaker? For example say the available short circuit current is 50KA and the instantaneous over ride value of the main breaker is 65KA. A short on the load side of the 4000 amp breaker will fall into the short time rating of the main 4000 amp breaker for which there is no published data for the switchboard bus structures. Damaged switchboard bus structures and bus supports are then possible before the 4000 amp breaker clears the 50KA fault.
Likewise, for a through fault condition where the selectively coordinated breaker settings are arranged for a short time delay between the 4000 amp main and the three 2000 amp feeders, the current that flows through the main bus may also result in damaged bus and bus structures due to this short time delay requirement.
In my experience, designers typically don't know about zone interlocking protection or if they do they don't request it often enough under these types of circumstances. Perhaps with focus on arc flash and selective coordination in the 2005 & 2008 NEC, people's understanding of zone interlocking will increase.
Zone Interlocking should help with the short circuit through fault condition described above to prevent short time bus bar and bus support damage in the main switchboard since the feeder breaker is supposed to trip immediately.
On the other hand, if the available short circuit current ahead of the selectively coordinated main 4000 amp breaker is high enough to reach even the Instantaneous Override rating of the main 4000 amp breaker or if the Instantaneous set point of the main 4000 amp breaker is set rather than over ridden, I don't see how a zone interlock system can be fast enough on instantaneous basis to respond to a 65KA through fault condition even with a zone interlock system in place. It seems to me that there would still be a race as to whether or not the 2000 amp feeder or the main 4000 amp breaker opened first because there is no way of knowing if the zone interlock system can communicate quickly enough on an instantaneous basis.
Any comments on this thread would be greatly appreciated.