peterb, you get a star from me. Anyone else who can shed some more light on vars & gens gets a star from me too. I still don't have a very qualitative understanding of what goes on when you start shoving vars around with generator systems, other than a vague sense that if you turn that pot just a little too far one way or the other that BAD THINGS start happening. Any further explanation of the BAD THINGS would be appreciated. Is this a resonance issue, with the plant or utility? Is this something purely internal to the gens, that they don't like to have vars shoved on to them -- and if so, why not?
I was recently on a project where they parallelled (3) 760kW, 480v generators full time with the utility, the utility tx normally only saw 100kW of load, the gens ran near rating. Due to the tx being unloaded, they would experience overvoltage. But if the gens shut down, they'd go to sever undervoltage. Someone came up with the bright idea to import LOTS of vars from the utility in an attempt to drop the voltage. And that seemed to help somewhat with the voltage issues. Someone else came up with the warning that on a similar installation, someone turned the dial a little too far and it launched the tie breaker out of the switchboard.
"Instability" sounds like a reasonable diagnosis there. Any more explanation of what's going on there would be appreciated.
I've asked this question of our local [#1 gen mfgr] dealer, seems I already knew more about this problem than they did [they were the one's that came up with the idea to suck vars from the utility in the first place].