MeinKaun11
Electrical
- Jul 21, 2013
- 19
Hi
I have attached a pdf file that shows breaker and bus arrangement for a 4.16 kV switchgear.
Background:
This project is replacement of a 1950 switchgear supplied by GE and has basic overcurrent protection on the feeders and 67 directional relays on the two main incomer feeders.
As part of the replacement, I have installed 751A relays on outgoing feeders and they would do most of the stuff typically part of feeder protection. for the bus protection, I am implementing bus blocking scheme using SEL 351-7 relays.
Question:
My dilemma is the existing 67 directional protection that was there before, why would I need a directional protection on incomers.
I would appreciate your input or any suggestions in regards to any other protection element that could be part of incoming protection scheme.
Regards,
I have attached a pdf file that shows breaker and bus arrangement for a 4.16 kV switchgear.
Background:
This project is replacement of a 1950 switchgear supplied by GE and has basic overcurrent protection on the feeders and 67 directional relays on the two main incomer feeders.
As part of the replacement, I have installed 751A relays on outgoing feeders and they would do most of the stuff typically part of feeder protection. for the bus protection, I am implementing bus blocking scheme using SEL 351-7 relays.
Question:
My dilemma is the existing 67 directional protection that was there before, why would I need a directional protection on incomers.
I would appreciate your input or any suggestions in regards to any other protection element that could be part of incoming protection scheme.
Regards,