Switching neutral in 120v control

Status
Not open for further replies.

electromike

Electrical
May 22, 2003
28
Does anyone have experience with switching the neutral instead of the "Hot" conductor in control circuits except in motor starter buckets. I have encountered this practice on a DCS system in a chemical manufacturing facility.I am told this is a safer practice in that all conductors in the field are already a grounded conductor and any shorts to ground will only switch "on" the respective circuit. I would like some input on this concept if anyone knows some specifics. Thanks.
 
Replies continue below

Recommended for you

If and when I come across my 1956 edition of the Canadian Electrical Code I'll check but I am pretty sure that the rule and practice was firmly established at least 50+ years ago. A long time ago when I was young I spent some time doing rewires on very old houses. It was very unusual to find a switched neutral. If one was found there was usually evidence that it was not original wiring but a modification.

Bill
--------------------
"Why not the best?"
Jimmy Carter
 
I don't know where I learned this misinformation, but I know it was long ago. Luckily I've only moved to more system design a few years ago, so I only have this crossed wiring in 20 systems; I can fix them as the come in on RMA. I wonder if UL would catch this when the system goes in for testing.

I did a web-search on this topic and it is amazing how much info pops up that switching the neutral is correct; scary. Luckily most of the entries also get corrected after a while.

Zapped
 
don't forget that a neutral only exsists in at least a 3 wire circuit. Many control circuits are isolated two wire cicuits that may or may not be grounded.
 
In this case neutral is what the NEC refers to as the "grounded conductor". No need for three phases or a wye system.
 