SWITCHING OVERVOLTAGE IN 30KV AND 6KV SWITCHGEAR

Status
Not open for further replies.

Parkpower

Electrical
Joined
Jan 18, 2009
Messages
18
Location
CA
Hi gentlemen,

Are surge arrestors needed to protect incoming cubicles and transformer or large motor feeder cubicles from switching overvoltage?

IF vacuum breakers are used,ABB 30kV and 6kV switchgear always install surge arrestors. But sometimes Siemens and Schneider do not install the surge arrestors.

Is there any IEC or IEEE code requirement concerning surge arrestors in switchgear?


Thanks,


Parkpower
 
Good companies observe good practices! Cheap ones seek excuses to become competitive.

SA at vacuum breakers are generally intended for taking care of overvoltages due to switching and it is a good practice. It is also a relatively inexpensive protection for unwanted surges coming from outside for any reason.


Rafiq Bulsara
 
IEEE std 1313.1 – IEEE Standard for insulation Coordination – Definitions, Principles and Rules – 1996 (R2002):
switching overvoltage standard are applied only to system with maximum voltage > 242kV.
 