EEJoe
Electrical
- May 31, 2017
- 2
Hi, I recently joined a plant where the E/I super has been performing switching the opposite of the way I was taught and I am looking for some references on switching order. In general I've always dropped loads first and opened from bottom up when de-energizing. For energizing, I've always started at the top of the system and worked down. The E/I super at our plant has been doing just the opposite, opening the main breaker first to de-energize, and when closing back in he will close all the downstream breakers first and then close in the main breaker.
His rational is that they've always done it that way and that doing it my way will take longer. My rational is that it is more stressful on the main breaker to close it with a load on it, there is potential for tripping due to inrush, and if there is a problem downstream it will be more difficult to find because the main breaker has tripped off.
Any opinions or reference material on the subject? I'm tying to find a technical reference to back up my point of view.
Thanks
His rational is that they've always done it that way and that doing it my way will take longer. My rational is that it is more stressful on the main breaker to close it with a load on it, there is potential for tripping due to inrush, and if there is a problem downstream it will be more difficult to find because the main breaker has tripped off.
Any opinions or reference material on the subject? I'm tying to find a technical reference to back up my point of view.
Thanks