Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations KootK on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Symmetrical faults.

Status
Not open for further replies.

johndaniel

Electrical
Feb 9, 2014
31
Hi folks
I am working on a short project to determine the detection of symmetrical fault occurence in loop system. Does anybody have a idea about this thing?

Thanks
 
Replies continue below

Recommended for you

An overcurrent element picks up in response to the fault. What more does your scheme need?
 
I want to find the direction of fault current in scheme.
 
In general, to determine the direction some type of 3-phase voltage sensing will be required at each overcurrent relay. The voltages are used to polarize the current detection.
 
To my way of thinking, most faults are unsymmetrical. Maybe a three phase fault would be the only symmetrical fault.

Are you looking at ways to detect symmetrical faults or any fault?
 
Ah, come on, there's lots of types of symmetry.

While a 3-phase fault is indeed symmetrical about any phase, an SLG fault is symmetrical about the faulted phase and a 2LG or LL fault is symmetrical about the unfaulted phase.
 
I am looking for the ways to detect the three phase faults on my system. As for any unsymmetrical faults(LG, LL, LL-G) the dominance of negative sequence components are high which could be used to determine the direction. But what about the three phase fault?
 
In power systems, "symmetrical" generally refers to symmetry of the sine wave. Faults other than three-phase are generally referred to as "unbalanced".

With appropriate voltage sensing and polarization, directionality of three-phase faults can be determined even with electro-mechanical relays. There's even a standard ANSI function code: 67

Here, let me Google that for you:


 
Directionality for 3-phase faults (yes, I know that's the common usage of symmetrical, but the question seemed rather odd) is actually easier than for the rest of the bunch; all that's needed is just the phase angle between voltage and current. When there's a fault and no negative sequence current any modern relay will use a positive sequence directional element. Now that negative sequence is just a numeric function it is readily available, but in the bad old days, phase directionality required comparison of phase-phase voltage angles against phase current angles.
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor