jraef
- May 29, 2002
- 11,359
I have inherited an old GE synchronous motor that I must control, and it has some information on the nameplate that I have not seen before. Maybe someone here has more experiance with this. (BTW, I have contacted GE already and have yet to get a response on the design spec., wiring diagram etc. They seem to move in geologic time.)
Here is the nameplate info:
Rated HP=1250 RPM=200 PF=.80
Volt.=4000 Hz.=60 Code=B
Amps=180.4 Frame=9464 Type=T8 (might be TB)
Excitation=250VDC Amps=72.1
Cont. HP=1437.5 Amps=191.0 Rise=90C Stator prot.=RTD
Specifically it is the last line on this plate that I have never seen before. What would be the difference between "Rated" HP and Amps vs "Continuous" HP and Amps? Which amp rating would I use to size the controller and protection system?
"Venditori de oleum-vipera non vigere excordis populi"