GTstartup
Electrical
- Mar 5, 2005
- 422
We tried this idea to verify synchronizing a 15KV 120 MVA generator across an SF6 Breaker. Note: we also did all the usual checks, backfeed etc.
We constructed six metal plates with insulated backs and taped them to the breaker pole frame right next to the insulators on each pole, for each phase, line side and generator side. We ran six wires from the plates outside the enclosure and using a 4 channel oscilloscope we were able to see the waveform at about 4V P-P induced. We were able to see that, when all phases are in phase, the synchroscope was at 12 and the synchronizer was sending the signal to close (breaker close command was disabled)
My question is - good idea or really, really dangerous and stupid?
PS we already did it with two units, OK I admit it, I've done it a few times before, once in a 230kV yard.
We constructed six metal plates with insulated backs and taped them to the breaker pole frame right next to the insulators on each pole, for each phase, line side and generator side. We ran six wires from the plates outside the enclosure and using a 4 channel oscilloscope we were able to see the waveform at about 4V P-P induced. We were able to see that, when all phases are in phase, the synchroscope was at 12 and the synchronizer was sending the signal to close (breaker close command was disabled)
My question is - good idea or really, really dangerous and stupid?
PS we already did it with two units, OK I admit it, I've done it a few times before, once in a 230kV yard.