Trying to commission a 11 KV, 2.5 MW steam turbine driven generator. The generator recently rewound and tested OK. Phase sequence also checked ok.
On synchronizing, the generator trips on reverse power every time. The turbine engineer says the turbine, the governor and the steam valve are ok.
I noted that on closing the breaker, the power factor goes haywire and the Woodwards Multifunction Relay reads about 100 amps in all 3 phases but the power is reading (-) 358 KW and the excitation is reduced to zero. (I will post two photos of the control board meters - before and after synch)in the following posts.
The AVR is Basler. I think the AVR is malfunctioning. Any other possible reasons for the RPR to act every time ?
Muthu
On synchronizing, the generator trips on reverse power every time. The turbine engineer says the turbine, the governor and the steam valve are ok.
I noted that on closing the breaker, the power factor goes haywire and the Woodwards Multifunction Relay reads about 100 amps in all 3 phases but the power is reading (-) 358 KW and the excitation is reduced to zero. (I will post two photos of the control board meters - before and after synch)in the following posts.