oftenlost
Industrial
- Jan 29, 2006
- 98
Surplus 250 HP, Westinghouse synchronous, 514 RPM, 440 volts, 261 AMPS FLA. Procured and inspected by service shop, good megger, surge test, rotor drop test and amortisseur appears to be original. Lead markings, 2 each of 1,2 and 3. XLE compressor with rotor on compressor crank
Installed and start attempted. Original GE 14 ohm resistor across rings. Motor accelerates to 250 to 260 RPM and hangs there. Start current 600 AMPS. Compressor unloader checked OK. Start resistor taken up in steps 18, 21 and then 26 with no apparent effect on speed. No arcing at rings or amortisseur. Talked to used motor vendor who indicated that he removed the motor personally from an idled plant site and had used the compressor for other purposes.
Installed and start attempted. Original GE 14 ohm resistor across rings. Motor accelerates to 250 to 260 RPM and hangs there. Start current 600 AMPS. Compressor unloader checked OK. Start resistor taken up in steps 18, 21 and then 26 with no apparent effect on speed. No arcing at rings or amortisseur. Talked to used motor vendor who indicated that he removed the motor personally from an idled plant site and had used the compressor for other purposes.