m.maran
Electrical
- Nov 29, 2017
- 4
Hello,
I've receaved an aparently new generator for maintance due to voltage control system failure.
But I've noticed that the problem was not the voltage control system.
The generator works fine without load. It reach the nominal voltage with normal field current and voltage.
But when any charge is conected to it the voltagem drops abruptly from 380 V to less thes 50 V.
It is a small synchronousm salient pole, two pole generator, 3-phase 8.5 kVA. I eliminated all the voltage control system and did some test directily applying and reading voltages and currents. I've use an independent manually controled voltage source.
1) I've already tested the stator without the rotor, aplying AC voltage on the terminals and current was equilibrated. So I do not belive that it I have problem with stator conections.
2) I´ve already tested the stator and rotor ohmic resistance and it is fine. Reforcing that conection in fine.
3) Open load test is ok, excitation is under expected.
4) Short circuit circuit, is not able to performe. The current doesn't rise with field voltage rise.
Does anybody has some idea about what is happening to this machine?
Thanks,
Best regards,
Maycon A. Maran
I've receaved an aparently new generator for maintance due to voltage control system failure.
But I've noticed that the problem was not the voltage control system.
The generator works fine without load. It reach the nominal voltage with normal field current and voltage.
But when any charge is conected to it the voltagem drops abruptly from 380 V to less thes 50 V.
It is a small synchronousm salient pole, two pole generator, 3-phase 8.5 kVA. I eliminated all the voltage control system and did some test directily applying and reading voltages and currents. I've use an independent manually controled voltage source.
1) I've already tested the stator without the rotor, aplying AC voltage on the terminals and current was equilibrated. So I do not belive that it I have problem with stator conections.
2) I´ve already tested the stator and rotor ohmic resistance and it is fine. Reforcing that conection in fine.
3) Open load test is ok, excitation is under expected.
4) Short circuit circuit, is not able to performe. The current doesn't rise with field voltage rise.
Does anybody has some idea about what is happening to this machine?
Thanks,
Best regards,
Maycon A. Maran