Tek-Tips is the largest IT community on the Internet today!

Members share and learn making Tek-Tips Forums the best source of peer-reviewed technical information on the Internet!

  • Congratulations cowski on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

System bonding jumper sizing NEC 250.30

Status
Not open for further replies.

PerigonRobert

Electrical
Joined
Nov 25, 2008
Messages
2
Location
US
I have a 1500 KVA (4160 Delta/ 480 Wye) transformer connected to a 3phase-3wire system (no neutral). Grounded at the X0 transformer terminal within the transformer secondary.

Secondary wiring is 6 parallel underground conuits with 3-350kcmils phase conducter per conduit.

My question is how large must the System Bonding Jumper be for each raceway (conduit)?
 
Each one must be fully-sized per the table, based on the total cross-sectional area of the phase conductors. If there is a ground fault in one conduit, virtually 100% of the ground current will flow in the ground wire inside that conduit, so it has to be fully-sized.
 
Thanks dpc --

The 12.5% calculation for 6 X 350kcmils =~ 300kcmils and to purcahse commerically available wire

I would need 350kcmils bare copper; therfore, each conduit would contain (3) 350kcmils insulated phase conductors and (1) 350kcmils bare copper cable.

Thanks again
 
Sounds about right. It doesn't have to be bare, BTW.

 
Status
Not open for further replies.

Part and Inventory Search

Sponsor

Back
Top