System bonding jumper sizing NEC 250.30

Status
Not open for further replies.

PerigonRobert

Electrical
Nov 25, 2008
2
I have a 1500 KVA (4160 Delta/ 480 Wye) transformer connected to a 3phase-3wire system (no neutral). Grounded at the X0 transformer terminal within the transformer secondary.

Secondary wiring is 6 parallel underground conuits with 3-350kcmils phase conducter per conduit.

My question is how large must the System Bonding Jumper be for each raceway (conduit)?
 
Replies continue below

Recommended for you

Each one must be fully-sized per the table, based on the total cross-sectional area of the phase conductors. If there is a ground fault in one conduit, virtually 100% of the ground current will flow in the ground wire inside that conduit, so it has to be fully-sized.
 
Thanks dpc --

The 12.5% calculation for 6 X 350kcmils =~ 300kcmils and to purcahse commerically available wire

I would need 350kcmils bare copper; therfore, each conduit would contain (3) 350kcmils insulated phase conductors and (1) 350kcmils bare copper cable.

Thanks again
 
Sounds about right. It doesn't have to be bare, BTW.

 