system neutral grounding

Status
Not open for further replies.

smur

Electrical
Sep 10, 2006
32
I used to work in a plant where they disallowed anyone grounding more than 1 system neutral at any time. So in a specific system such as 13.8kv or 3.3 kv etc, you can only have 1 system neutral grounded. Any reasons for this?
thanks
 
Replies continue below

Recommended for you

If it was an impedance earthed system, multiple earths increase the available earth fault current. If it was a four-wire system then multiple earth connections lead to current flow in the bulk of earth, a condition which is normally prohibited and even if permitted can cause strange behaviour of protection and control equipment.


----------------------------------
image.php
Sometimes I only open my mouth to swap feet...
 
Thanks. It is impedance earthed system Resistance. But I have also worked at places where people have muliple system grounds. Ofcourse you must set the ground relays accordingly. Is ther any benefit beteen the 2 systems in any manner?
 